Burned PSUs
ehsab
Burned PSUs
Wed Jun 20, 2018 11:37 am
I've had my first Netonix Switches die on me.
They died with a couple of days between them, both with burned PSUs.
Both of them was on UPSes.
I'd like to see if someone might tell me from the pictures if it could be problems from the AC side or the DC side (ports).
Backside of PSU1
https://imgur.com/OaGXNfH
Frontside of PSU1
https://imgur.com/jB4c1Gs
Backside of PSU2
https://imgur.com/PlhZnLX
Kind Regards
ehsab
Re: Burned PSUs
Wed Jun 20, 2018 11:43 am
That type of damage is from the AC power source and or came in the AC ground from poor grounding.
My bet is the switchboard is probably OK.
Test the switch board with a 48V DC power source and take it through the Bench Test as described here: viewtopic.php?f=6&t=2780#p19221
Next time please upload your pictures as described in my post footer.
ehsab
Re: Burned PSUs
Wed Jun 20, 2018 12:00 pm
Thank you for quick answer.
What happend in the PSU due to poor grounding? Seems like the burned area is on different places.
Is it possible to buy PSUs separetly, if the switchboard is ok?
Kind Regards
Re: Burned PSUs
Wed Jun 20, 2018 2:22 pm
What I mean by poor grounding is if the the electrical service ground rods are insufficient and a surge comes into the electrical service everything with a surge protector or similar circuitry tries to shunt that excess current to the ground and there is a ground plug on the AC cord so that ground current can actually come into the power supply from the ground plug trying to get to the tower ground through the switch through the Ethernet cable to the device on the tower through the tower to the tower ground rods but the power supply tries to isolate DC output from Earth ground and poof.
Often when the power supply is damaged from a surge it does not damage the switch board....NOT A GUARRANTEE
WHich is why I suggested you test the switch board with either another power supply from another WISP Switch of same model or carefully provide 48V to the board connector then BENCH TEST IT as explain in the link I provided above.