NETONIX SWITCH FAILURES CONNECTED TO BATTERIES TO LARGE AMP.

DOWNLOAD THE LATEST FIRMWARE HERE
JAGUZU
Member
 
Posts: 3
Joined: Tue Jun 25, 2019 1:19 pm
Has thanked: 3 times
Been thanked: 1 time

NETONIX SWITCH FAILURES CONNECTED TO BATTERIES TO LARGE AMP.

Tue Jun 25, 2019 1:23 pm

good morning, please we need your help or information to a problem we have with your netonix dc 250 12 vdc switches, which of the 4 that we have bought, 2 are out of service for the following and has already happened 2 times the same, so we want to know what your recommendation is and how we could connect these switches to our battery banks of 2 volts (800 amp) x 6 = 12 volts, but that we have realized that as our battery charger is 40 amps or have a 100 ampere, so you can charge these batteries faster or in one case is a 2000 watts xantrex prosine, which brings a large amperage charger that while the batteries are charged there is no problem with the switch netonix work very well, but when the power goes and it comes back and starts the battery chargers to send the load with the respective capacity of amperage, the switches are burned and they stop working these are immediately useless and there would be to send them to repair, but for this reason we have not bought more switches for fear of burning, then the question is whether the charger sends great amperage to the batteries where these netonix switches are connected directly, as we could do so correct ?, so that these do not burn or are out of service, thank you for your response and solution.

User avatar
lligetfa
Associate
Associate
 
Posts: 1186
Joined: Sun Aug 03, 2014 12:12 pm
Location: Fort Frances Ont. Canada
Has thanked: 305 times
Been thanked: 381 times

Re: NETONIX SWITCH FAILURES CONNECTED TO BATTERIES TO LARGE

Tue Jun 25, 2019 2:34 pm

You cannot have too many amps supplying the switch. The switch will only draw the amps it needs. My guess is you are burning up switches due to a ground potential shift and need to examine your grounding and bonding.

User avatar
sirhc
Employee
Employee
 
Posts: 7347
Joined: Tue Apr 08, 2014 3:48 pm
Location: Lancaster, PA
Has thanked: 1597 times
Been thanked: 1317 times

Re: NETONIX SWITCH FAILURES CONNECTED TO BATTERIES TO LARGE

Tue Jun 25, 2019 3:02 pm

Les is correct above.

Below is an exert from an email I just sent to a Distributor in another country about ground current and how to educate their customers (PLEASE READ):


Yes, best practices is to stress to customers the importance of proper grounding especially with the SMART DC units we sell as their power supplies are not isolated which means that earth ground and DC negative are bonded in the switch.

Most DC chargers also bond earth ground to DC negative and lastly “most” radios WISPs use such as UBNT, MIMOSA, Cambium, and so on also bond POE DC negative to chassis/earth (tower) ground.

Then the Ethernet cable becomes the bond between 2 ground potentials.

If there is a bad electric motor or other appliance such as an AC compressor that is going bad it can inject ground current often at harmonics far above 50/60 Hz which damages the switches and or radios.

Also ground current can come from the electrical provider as your electric company usually hands off hot/neutral/ground and the ground they hand you is bonded to neighboring electrical services so if you have say an industrial park nearby and they have failing electrical motors and poor grounding this ground current can enter your site from the provider.

It is always best practice to add additional electrical service ground rods to handle any ground current coming in from off site and or ground current generated on site. If the service ground rods are poor and there is a surge of ground current it will seek out the path of least resistance which is often the nicely newly installed tower ground rods and the path for the ground current is through the switch and across the Ethernet cable through the radio to the tower to the tower ground rods – POOF.

Often ground current damage occurs during rain events as water wicks down the service ground rods increasing their resistance to ground. Often rain events are during electrical storms and people often mistake ground current damage as storm damage (surges) and this is incorrect.

It is also practice in the telecom industry to make sure there is ONE ground potential for the entire site meaning BOND electrical service ground rods to tower ground rods with heavy gauge wire.

I have been a WISP for 20+ years and until I understood what ground current was I lost equipment all the time. Now I only lose equipment when someone messes with the grounding improvement we put at sites we use that are leased and are messed with by the site owner or other tenants of the tower.

Now as of this past few months we made changes to our AC switch models to make them more isolated in hopes to better survive poor grounding but our SMART DC models WS-8-150-DC / WS-12-250-DC / WS-26-500-DC will require a redesign of the power supplies which we are contemplating but again if people do proper grounding this is not an issue.

Rules of thumb for WISPs:
Add NEW additional ground rods to existing electrical service and or double the usual required # of ground rods for NEW electrical services. Here in the US code requires 2 so we add 2 more = 4

Always bond electrical service ground rods to tower grounding system if at all possible. If not then for sure add additional service ground rods to make sure tower ground path never looks better than service ground path.

Never plug in cable to ports with POE already turned ON and always make sure the device is compatible and you use the correct POE option. The second most common RMA damage is from shorted cables or incorrect POE option applies which fries the Ethernet Transformer and sometimes the entire switch as it can create a conductive path for POE current to enter the PHY/SOC, all depends on how the Ethernet Transformer fries.

Here are 2 good posts to make sure customers read:
viewtopic.php?f=6&t=1178#p8809
viewtopic.php?f=6&t=1215#p9040

With the WS-12-DC and WS-26-DC make sure the power supplies they use are ISOLATED power supplies meaning earth ground is not bonded to DC negative and follow the grounding suggestions above.

Ground current damage usually results with the current sensors being damaged whereas shorted cables usually does not harm the current sensors it just fries the Transformer and sometimes the SOC. Ethernet Transformer damage usually can only be seen when the Transformer is removed and flipped over as seen in previous pictures I sent you.

Another common mistake people do is run Ethernet Copper cable from one device on one electrical service/panel to another device on another electrical service/panel which will have different ground potential and thus the Ethernet cable becomes the BOND or ground loop. Now ground current from the one service with the higher resistance to ground will try and cross the Ethernet Cable. One should always use FIBER when connecting devices across different ground potentials.

99% of all WISP equipment damage is from ground current (I own a WISP)
Another common cause for damage is a shorted cable or incorrect POE option applied to device.

Here are some good posts on grounding:
viewtopic.php?f=30&t=2786#p19279
viewtopic.php?f=30&t=1816
viewtopic.php?f=30&t=188
viewtopic.php?f=17&t=1786&start=30#p13447
viewtopic.php?f=30&t=1429

Read the posts above but the basics are as follow:
Tower ground rods must be bonded to electrical service ground rods HEAVY #2 wire.

I always add 1 or 2 “new” ground rods to older existing electrical services.

In the event bonding service rods to tower rods is not possible then definitely add additional NEW ground rods to electrical service to help prevent service ground current from ever seeing tower ground rods as a better path to ground.

One last thing, Electrical and Ethernet Surge suppressors will do nothing to prevent ground current surges and damage. Think about it, how surge suppressors work is to shunt excess voltage to ground but there is nothing in them to prevent ground current from simply passing right through.

In fact I use ZERO Ethernet Surge suppressors in my entire WISP, I do though use GOOD electrical surge suppressors to combat electrical surges.
Support is handled on the Forums not in Emails and PMs.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.

JAGUZU
Member
 
Posts: 3
Joined: Tue Jun 25, 2019 1:19 pm
Has thanked: 3 times
Been thanked: 1 time

Re: NETONIX SWITCH FAILURES CONNECTED TO BATTERIES TO LARGE

Tue Jun 25, 2019 4:13 pm

Thank you very much for your observations, I will take you into account, and I will do the tests with the switch that we still have working, if you could recommend me to acquire the DC to DC account and that allows me to protect the switches from these inconveniences and that allow to pass the amperage of the xantrex prosine that is 100 amp, I would like them.

User avatar
lligetfa
Associate
Associate
 
Posts: 1186
Joined: Sun Aug 03, 2014 12:12 pm
Location: Fort Frances Ont. Canada
Has thanked: 305 times
Been thanked: 381 times

Re: NETONIX SWITCH FAILURES CONNECTED TO BATTERIES TO LARGE

Tue Jun 25, 2019 7:16 pm

JAGUZU wrote:...our battery charger is 40 amps or have a 100 ampere...

If your DC negative is earthed at the charger and you have a long or light gauge wire feeding the batteries and/or Netonix, the resistance will, under high current, act as a series resistance voltage divider resulting in a ground potential shift.

If the grounding point of the charger is shared with the utility AC mains ground, then electrical disturbances on the grid can also cause ground potential differences.

It is important that the bonding wire be heavier gauge and a shorter run than the supply leads.

JAGUZU
Member
 
Posts: 3
Joined: Tue Jun 25, 2019 1:19 pm
Has thanked: 3 times
Been thanked: 1 time

Re: NETONIX SWITCH FAILURES CONNECTED TO BATTERIES TO LARGE

Wed Jun 26, 2019 6:41 am

Thank you very much for your observations

Return to Hardware and software issues

Who is online

Users browsing this forum: Google [Bot] and 23 guests